My 5 Ton AC condenser worked well last year but it is not working this year.
Both compressor and condenser fan are not running. The situation is below:
1. There is a AC power 110V between 2 hot lines on the contactor input terminals before turning on the AC. But this power is gone after turning on AC (24 V on). So both motors can't start.
2. When turning off the AC (24 V off), the 110 V is back.
What's wrong with this problem? Somewhere short? Relay bad?
Are all wires connected correct (see attached picture and diagram)?
Brand: Bryant
Product: 561CJX060000AAAA
Model: 561CJ060-A
Serial: 2300E23243
(see attached model plate)
Please advise, thanks.
Rick
carmon 04-30-2012 10:00 PM
you require 230 vac at the line side of the contactor...:eek:
rliu 04-30-2012 11:01 PM
I know the compressor is running at 230V. But each line in is 115V from the power circuit. How can get 230 between 2 input lines?
Doc Holliday 04-30-2012 11:14 PM
You need to check across one leg to the other, from one terminal to the other at the contactor, and see if you have 240-ish volts. If not, you've got an electrical problem such as a bad breaker.
biggles 04-30-2012 11:22 PM
230V with meter on both in coming line wires to the top of the contactor...and 24Vs on the 2 blue wire nuts.witht he condenser disconnect off that contactor should pull in from a call for cooling from the stat....don't check the incoming 230 to ground check between legs each 115V to ground
Doc Holliday 04-30-2012 11:28 PM
Also, do you have an electrical disconnect at the unit, with fuse perhaps? Check across the poles there as well.
rliu 05-01-2012 12:18 AM
So you mean between 2 black lines to the input of contactor should be 220vac, but I measured it is 110vac only. I'll check it on the circuit beaker. But I wonder why this 110vac gone when turning 24v switch on? Will this problem go away when the 220vac is normal? Thanks.
Doc Holliday 05-01-2012 02:54 AM
it should as far as the condenser being able to run but outside of the voltage problem who can tell..?
You're missing one leg of 120v.
rliu 05-01-2012 07:58 PM
I found one input line burned in the circuit beaker box but don't know why.
Question:
Is my compressor still good as the follow measurement?
CR = 0.4 ohm (blk-yel)
CS = 1.9 ohm (blk-blu)
SR = 2.2 ohm (blu-yel)
I have known SR=CR+CS, from this formula, compressor should be fine but I wonder why the resistance is so small between 3 terminals.
Please advise: Is the compressor good (not short)? It is 5 ton compressor.
carmon 05-01-2012 09:36 PM
it will be fine... try it you will find out fast...