-   -   AC compressor starts only when manually depress contactor (http://www.diychatroom.com/f17/ac-compressor-starts-only-when-manually-depress-contactor-155349/)
tappan67 08-30-2012 06:51 PM
Hello,
Any expertise would be appreciated.Payne outside ac unit will start with manual engagement of contactor.
New cartridge fuses outside at service disconnect
cant detect 24v at low side contactor outside ac
can't detect 24v in furnace on the board labeled: 24vcom and y/y2 .this is the where the low side of ac outside ac unit connects outside.
Tappan67
Doc Holliday 08-30-2012 06:57 PM
R is your 24 volts at the board. The board does not send power to the y terminal until the stat is on call for cool. Then it's y and com.
Is there a drain pan under the unit? Does it have a switch attached to the side? Is there water in the pan? If there is water in the pan then lift the switch from out of the water so the float device lowers while on call for cool.
Let us know.
Doc Holliday 08-30-2012 07:02 PM
first check for 24 volts from the R terminal on the board, to C or to the actual cabinet. make sure that if there is a door switch on the furnace that it is pushed in to allow power to the board, while the doors are removed. once it's confirmed there is or is not 24 volts at the control board we can assist you better.
Even easier than that, will the fan only come on from the thermostat? Heat? If so then you have 24 volts at the board.
tappan67 08-30-2012 07:03 PM
Hi Doc,
I cant get to the sheet metal screws that open up where I think you asked. There appears to be a drain pipe that makes acces to the those screws difficult.
I'll get it open and get back.
Thanks:thumbsup:
Doc Holliday 08-30-2012 07:04 PM
I meant under, not inside, the entire unit. What I'm talking about would be a secondary drain pan. What type of unit is this, electric air handler or gas furnace? Is this horizontal or vertical, closet or attic or basement? Can you take a pic?
tappan67 08-30-2012 07:23 PM
Need a flexible socket extender there is schedule 40 pipe blocking access. Once I have one I will reply.
biggles 08-30-2012 07:29 PM
shut the disconnect off outside on the condenser...remove the stat off the subbase jump R to Y on the stat...contactor on condenser should be in....if not jump R to Y on board no againn...check for 24Vs at the pair of low voltage wires out of the brown wrapped bell wire......remove terminals off contactor coil ring out should be a resistance or shorted...if no ction on the metr set in OHMs the coil in the contactor is open need a new one..
tappan67 08-31-2012 11:33 AM
1 Attachment(s)
Ill try to attach a photo.
Its a vertical gas furnace in garage.
Model carrier weathermaker 8000 ts
The furnace side functions like normal its the just the ac that wont start
when therm calls for cooling.
tappan67 09-04-2012 04:47 PM
Making progress finally. Jumped at stat nothing happened. Jumped at furnace r to y and I could hear the contactor click on and off. Powered up at service connect and now ac is running fine. My problem seems to be between furnace board and thermostat. What should I try next.
thanks
steve:thumbup:
tappan67 09-04-2012 05:55 PM
biggles,
I just double checked and reattached wires at stat and it did not make the ac compressor turn on. Do you think I should buy a new thermostat? Any help is very appreciated. Thanks
Steve
Missouri Bound 09-04-2012 06:46 PM
If you jumpered it at the stat and nothing happened it's most likely a wiring issue. Don't buy a thermostat yet. Any way to check out the wiring?
tappan67 09-05-2012 12:09 PM
I took each wire off stat checked for wear andreattatched. Still wouldn't starts AC. Not sure what next step should be.
JJboy 09-05-2012 02:17 PM
cable from stat to furnace
Sent from my iPhone using DIY Forum
Missouri Bound 09-05-2012 07:34 PM
Run a new wire from the stat to the furnace. Is that possible for you to do?
tappan67 09-15-2012 01:32 PM
I was in the process of making a short wire to hook up my old stat to board in furnace so i could stand right there and not have to pull wire to see if it would work and noticed a wire that had come off board. I stripped and reattched and put stat back on wall and it worked!! :thumbup:
Thanks to all for your expertise.:thumbsup:
Steve