Old 10-18-2012, 08:07 PM   #1
Newbie
 
Join Date: Oct 2012
Posts: 2
Share |
Default

ac compressor running without blower/thermostat won't turn off compressor


Hi! I'm hoping to get some help with my girlfriend's ac unit before having to call a tech out. I noticed today that the compressor on the outside unit was running but the blower was not pushing any air inside the house. The temperature was set to 76 on the thermostat and was 76 in the house, so that was good. I set the temp down to 74 and the the blower came on and was pushing air through the vents, also good. I set the thermostat to 'off', which turned off the blower, but the compressor was still running and did not turn off at all. At this point I have shut the unit off at the breaker to avoid possible future damage. I made my way to the roof and there was significant ice build up in the unit. I opened the service panel and the checked the contactor, which looked fine. I had my girlfriend turn the breaker on and off and the contactor moved in and out like it should, so its not stuck closed. Wires from the thermostat to the board on the unit look fine and are wired correctly. I am thinking it is just a bad thermostat, but before making a run out to pick up a new thermostat I want to see if there are any other quick things I should be checking. Any ideas are greatly appreciated!

cphaller is offline   Reply With Quote
Old 10-18-2012, 08:38 PM   #2
Member
 
Join Date: Oct 2011
Location: pa
Posts: 4,275
Default

ac compressor running without blower/thermostat won't turn off compressor


Quote:
Originally Posted by cphaller View Post
Hi! I'm hoping to get some help with my girlfriend's ac unit before having to call a tech out. I noticed today that the compressor on the outside unit was running but the blower was not pushing any air inside the house. The temperature was set to 76 on the thermostat and was 76 in the house, so that was good. I set the temp down to 74 and the the blower came on and was pushing air through the vents, also good. I set the thermostat to 'off', which turned off the blower, but the compressor was still running and did not turn off at all. At this point I have shut the unit off at the breaker to avoid possible future damage. I made my way to the roof and there was significant ice build up in the unit. I opened the service panel and the checked the contactor, which looked fine. I had my girlfriend turn the breaker on and off and the contactor moved in and out like it should, so its not stuck closed. Wires from the thermostat to the board on the unit look fine and are wired correctly. I am thinking it is just a bad thermostat, but before making a run out to pick up a new thermostat I want to see if there are any other quick things I should be checking. Any ideas are greatly appreciated!
shut off switch to unit open thermostat and remove the wire on the y terminial...see if outdoor unit stops after you power back up...that controls the outdoor contactor for a/c...ben sr

ben's plumbing is offline   Reply With Quote
Old 10-19-2012, 04:17 PM   #3
REP
Member
 
Join Date: Jul 2011
Posts: 615
Default

ac compressor running without blower/thermostat won't turn off compressor


I can't imagine its the stat,but if it is then please don't get a cheap copy.Get a Honeywell or a White Rogers.It might be a heat pump with the defrost acting up.
REP is offline   Reply With Quote
Old 10-19-2012, 04:51 PM   #4
Member
 
Join Date: Oct 2011
Location: pa
Posts: 4,275
Default

ac compressor running without blower/thermostat won't turn off compressor


hey rep I guess we have to wait for op to get back to us....must not be that important ...ben sr
ben's plumbing is offline   Reply With Quote
Old 10-19-2012, 05:13 PM   #5
Newbie
 
Join Date: Oct 2012
Posts: 2
Default

ac compressor running without blower/thermostat won't turn off compressor


Hey guys thanks for the suggestions. So I waited for the condenser to thaw and tried pulling the y wire. And the compressor is still powering up with the thermostat set to off. I'm thinking there is a bigger problem.
cphaller is offline   Reply With Quote
Old 10-19-2012, 06:26 PM   #6
Member
 
Join Date: Oct 2011
Location: pa
Posts: 4,275
Default

ac compressor running without blower/thermostat won't turn off compressor


Quote:
Originally Posted by cphaller View Post
Hey guys thanks for the suggestions. So I waited for the condenser to thaw and tried pulling the y wire. And the compressor is still powering up with the thermostat set to off. I'm thinking there is a bigger problem.
ok now pull the the wire off y terminial on control board..... see if it stops...if not check contactor in a/c unit may be a bug got zapped in contactor and its stuck... or bad 24 volt coil for contactor....ben sr

ben's plumbing is offline   Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Air Compressor Fittings - Differences? roasted Tools 3 09-19-2012 08:15 PM
Issue with compressor unit boast HVAC 2 08-29-2012 10:04 PM
3 phase 230/460 air compressor install questions DinAZ Electrical 7 10-21-2011 10:28 PM
portable ac compressor tripping breaker :( tamar120 HVAC 7 04-29-2010 04:48 AM
Air Compressor Timer 69-er Electrical 7 10-02-2007 03:40 PM




Top of Page | View New Posts

Copyright © 2003-2014 Escalate Media. All Rights Reserved.