5 Ton Compressor Electrical Supply - HVAC - Page 5 - DIY Chatroom Home Improvement Forum
Closed Thread
Old 08-14-2012, 09:33 PM   #61
I'm Your Huckleberry
Rewards Points: 2,270
romEx, not romAx.
That is all.
Thanks.
Doc Holliday is offline
Old 08-14-2012, 09:35 PM   #62
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
Originally Posted by stickboy1375 View Post
I've been saying this the entire time.. Finally you got it... Did you not read that the motor contains the over current protection?
Overload?
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline
Old 08-14-2012, 09:39 PM   #63
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Originally Posted by electures View Post
Overload?
After a few beers they all seem the same.
stickboy1375 is offline
Old 08-14-2012, 09:40 PM   #64
electures's Avatar
I am curious to know if the disco will be fused or non-fused.
Old 08-14-2012, 09:41 PM   #65
E2 Electrician
I doubt it needs to be fused, I have yet to come across a unit that requires fuses...
Old 08-14-2012, 10:21 PM   #66
Licensed electrician
Rewards Points: 1,876
Originally Posted by turnermech View Post
are you saying you are not required to size the wire based on the breaker?
The breaker size is exactly how I size the wire. I size the breaker to the unit and run the wire that will carry the amps of the breaker.
You do not need to size the wire to the breaker ampacity for an A/C unit. The breaker and wiring are sized from the nameplate data. The wiring is sized for the running load. The breaker is sized for the startup. To run 50 amp wiring because the unit requires a 50 amp breaker for startup is a waste and completely unnecessary.
Jim Port is offline
The Following 2 Users Say Thank You to Jim Port For This Useful Post:
stickboy1375 (08-14-2012), Venter (08-14-2012)
Old 08-14-2012, 10:22 PM   #67
E2 Electrician
I think this was mentioned and forgotten...
Old 08-14-2012, 10:24 PM   #68
And it's what someone who does not know the code would do.
Venter is offline
Old 08-14-2012, 10:37 PM   #69
I don't think anyone said conduit would be cheaper. The comment was made that should a conduit system be used you could take advantage of the higher ampacities afforded to THWN due to the higher temperature column and run the #10s.
You could run the 8-2 NM inside and switch to #10 THWN at the disco to the unit and be compliant.
I also don't know why you would be so scared to ask an inspector for an citation of the violation he thinks you commited. They are required to cite the violation. If they can't show you it should pass and the inspector should learn from this. If they are correct you should learn something and both move on.
BTW, it is Romex, a trademarked brand name, not romax.
Jim Port is offline
Old 08-14-2012, 10:41 PM   #70
E2 Electrician
I totally dislike when a simple thread has to go to beyond 50 posts when the correct answer was given in post 3, a new thread should have been started and resolved the unawareness of the actual code vs what I think it should be scenario... This just screws up the OP and scares them away.
Old 08-15-2012, 07:22 AM   #71
Willing to listen
Rewards Points: 223
FWIW I appreciated the discussion and education. I doubt I will ever be wiring a unit but it's nice to have a better understanding of how the breaker size, wire size, and MCA data are related.
Done That is offline
Old 08-15-2012, 04:13 PM   #72
E2 Electrician
Here is the real breakdown, the manufacture does all the math required by article 440 of the NEC, they will take the largest motor and add 125% to this number then add all the other motors, this number becomes the MCA, Minimum circuit ampacity, Now, since we are dealing with motors, and they contain there own internal thermal protection, (circuit breaker) we can add up to 225% to the MCA to come up with a maximum circuit breaker, since this breaker is only supplying ground-fault and short-circuit protection...
Its pretty easy to grasp with a little knowledge, but this topic just leaves so many people in disbelief, because of the fact you have a larger breaker size than wire size...
The Following User Says Thank You to stickboy1375 For This Useful Post:
Done That (08-15-2012)
Old 08-15-2012, 11:12 PM   #73
Registered User
Rewards Points: 526
I feel the questions from the OP have been well answered by now. Posts have been removed for breaking the forum rule; treat other members with respect found at the bottom of every page under "Privacy statement" or "Terms of service". Thread closed. Gary
Gary in WA is offline
Closed Thread
Tags
electrical , electrical code , hvac , wiring
Distance between HVAC supply and return vents atlantatd HVAC 4 04-13-2011 08:30 PM
Need help fast please re hydronic boiler water supply and backflow DanDaMan HVAC 6 12-11-2010 02:26 PM
Supply valve to bath faucet doesn't stop water Kurt123 Plumbing 2 09-05-2010 09:48 PM
Extending Water Supply Box In Laundry Room hsl Building & Construction 0 11-18-2009 09:21 AM
help w/ duct sizes & new supply locations palex1915 HVAC 0 10-13-2009 07:52 PM