5 Ton Compressor Electrical Supply - HVAC - Page 3 - DIY Chatroom Home Improvement Forum
Closed Thread
Old 08-14-2012, 05:51 PM   #31
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Originally Posted by turnermech View Post
I talking about 10-2, 8-2, & 6-2 romax. I think some of these issues come for some are talking wire in conduit. the amp rating are not the same for each.
I stand by my statement of 10-2=30 amps 6-2 = 60 amps (8-2 I always have to look up as far as it being 40 or 45 and I don't carry the code book home from the office). I would say the OP is not going to run conduit he is going to run romax.
I clearly stated that in my first post.
stickboy1375 is offline
Old 08-14-2012, 05:52 PM   #32
"The loads imposed have already been calculated by the manufacturer. If they did not want to allow #10 they should have raised the minimum circuit ampacity on the dataplate."
if they raise the MCA then they may not sell a unit for a case where wire is already ran. They would perfer to have a larger wire but they don't want to lose a sale. Anyone can run min that is why it is there. You can also come back to reset breakers for free.
turnermech is offline
Old 08-14-2012, 05:53 PM   #33
so did I. It would appear we both missed it.
Old 08-14-2012, 05:53 PM   #34
E2 Electrician
Originally Posted by beenthere View Post
Not always. under sized wire to an A/c or heat pump can cause it also.
You run what you want for your customers, I'll run wire sized more for the max amp, and lower voltage drop.
Good luck with that.
Old 08-14-2012, 05:56 PM   #35
An old Tradesmen
Rewards Points: 7,372
Not hard to do. I stay at 2% or less voltage drop on resi units.
beenthere is offline
Old 08-14-2012, 06:03 PM   #36
Licensed electrician
Rewards Points: 1,628
There is no need to come back to reset a breaker. The breaker is sized for the startup. The wire size has no bearing on the max breaker size.
Jim Port is online now
Old 08-14-2012, 06:07 PM   #37
An old Tradesmen
That's insane and a waste of money but I'm not buyin from you, so like I said good luck with that... And yes, the lights will still dim.
Cost more upfront. Saves far far more in operation over the life time of the equipment.
I tell people upfront, I will be more expensive then others. So if your looking for low price, don't waste either of our time. If your looking for performance, then I can come out and see what you need.
Old 08-14-2012, 06:16 PM   #38
are you saying you are not required to size the wire based on the breaker?
The breaker size is exactly how I size the wire. I size the breaker to the unit and run the wire that will carry the amps of the breaker.
Old 08-14-2012, 06:18 PM   #39
E2 Electrician
I've been saying this the entire time.. Finally you got it... Did you not read that the motor contains the over current protection?
Old 08-14-2012, 06:20 PM   #40
some are talking cost. I would think 6-2 romax is cheaper than 10 wire and the conduit. And then there is the labor cost. It has got to cost more to run conduit. Why would you run conduit from the panel to the disconnect in most residential applications. Some make it seem as 6-2 romax would cost more. I can't see it.
Old 08-14-2012, 06:20 PM   #41
you would be fighting with the local inspectors here. Nothing like a code book battle I guess. that is why i asked what I did before about from the disconnect. I have seen this argument fail here.
Old 08-14-2012, 06:25 PM   #42
An old Tradesmen
Just show them the code in the book. They can't argue to well against their own book.
Old 08-14-2012, 06:31 PM   #43
E2 Electrician
I'm here to help, but I'm out at the moment, I'm more than willing to spend the time to help you understand this.
Old 08-14-2012, 06:35 PM   #44
win 1 loose the next 10. I stay on the good side of inspectors unless they are unreasonable. In this case I would be agreeing with them.
Old 08-14-2012, 06:55 PM   #45
What would be the benefit of running individual strands of 10 wire in conduit instead of 8-2 or 6-2 romax? I can not amaigine it would cost less when you factor the conduit cost and added labor. I can't see none other than saying “I was able to successful run the smallest wire possible for the unit”. Do we agree that it can't be done on 10-2 romax?
Closed Thread
Tags
electrical , electrical code , hvac , wiring
Distance between HVAC supply and return vents atlantatd HVAC 4 04-13-2011 08:30 PM
Need help fast please re hydronic boiler water supply and backflow DanDaMan HVAC 6 12-11-2010 02:26 PM
Supply valve to bath faucet doesn't stop water Kurt123 Plumbing 2 09-05-2010 09:48 PM
Extending Water Supply Box In Laundry Room hsl Building & Construction 0 11-18-2009 09:21 AM
help w/ duct sizes & new supply locations palex1915 HVAC 0 10-13-2009 07:52 PM