3 Ton Evap 2 Ton Compressor - HVAC - Page 4 - DIY Chatroom Home Improvement Forum
Old 03-12-2014, 09:32 AM   #46
well let me think out load here. In heat mode I will have a 3 ton evap so there is no chance of liquid getting back to the comp, Super heat should be high. Im going to send way super heated vapor to the indoor coil (condenser), Discharge line I would think would be about 180 degrees or even higher ? as long as I am blowing 1200 cfm I should get a delta T of 30 maybe even 40 ? ? ? but if I don't still would be less liquid coming back to the evap - compressor right? Seems super heat would just keep getting higher and higher though as well as discharge?
How can I check the CFM of the fan without a hood or tearing up the duct work?
Once again thanks for all the great help!
subcool is offline   Reply With Quote
Old 03-12-2014, 04:04 PM   #47
An old Tradesmen
Rewards Points: 7,802
59 would be 2 tons. 3 tons would be 71 plus or minus depending on manufacturer.
Old 03-13-2014, 03:15 PM   #48
ok I have solved the problem I think. Local distributor here, called this morning said 40K btu 3 ton air handler fell off the fork lift. I have a brand new 15 year warranty air handler for 150.00. It is only 80 percent, but hey backup heat doesn't need to be 90% :-)
Old 03-13-2014, 03:47 PM   #49
An old Tradesmen
You still need to change the piston to the right size for the condenser.
Old 03-15-2014, 07:18 PM   #50
Man what the hell is going on? I changed pistons, blew nitrogen through lines. had to blow piston out because it was tight, so there cant be a restriction. Subcool is 21 and super heat is 35. low side is 41 Vsat of 18 or so. High side 153.5. I did not change the fan yet, but low flow should lower superheat right? I check the temp drop across the filter les than 1. In heat mode Im getting a discharge of 318 and 135 degrees (DB is 68) my liquid kine is 95.3 and 85.3 degrees. That give me a -30 subcool. Im actually picking up superheat in the indoor coil now in heat mode. How in the hell can I pick up heat?
oh yeah my delta T in both modes is about 30 degrees. So the freaking thing is working, but cant figure out how it is working. and if im getting liquid back in heat mode
Old 03-15-2014, 08:08 PM   #51
An old Tradesmen
Had to blow piston out? New piston may be sticking also then.
Indoor coil being so small will never work right in heat mode.
Sounds like their is a flow issue with the indoor coil itself.
Old 03-16-2014, 10:01 AM   #52
The piston was in the housing, so I could not get down there to get it. I just blew the opposite way and it shot across the room. so the evap is not blocked. What is killing me is this worked 2 weeks ago. I changed the compressor and LLFD and now it will not work.
In heat mode with the smaller coil sub cool will be low, but picking up superheat? Man I wonder if my gauges could be screwed up? or temp probe? I will check all those today, I just can not figure this out! I am also going to totally remove the piston and see what SC/SH numbers I get. lol
The only other thing I can think of, is I did not actually look at the piston to make sure it was a 76 maybe he gave me the wrong one.
Old 03-16-2014, 12:12 PM   #53
An old Tradesmen
Check the piston size.
What killed the other compressor.
Old 03-16-2014, 02:30 PM   #54
The other compressor has a power surge. Blew-out the terminals, all but the common terminal.
Old 03-16-2014, 08:10 PM   #55
An old Tradesmen
Did you gt the piston size checked.
Old 03-17-2014, 09:02 AM   #56
I have not had time to check to size but the bag the piston came in said 73.
Old 03-19-2014, 04:11 PM   #57
ok taking another look at this. The piston was a 73 should be fine. I was going to check the super heat(in heat mode), to make sure Im not getting liquid back to the compressor. Vsat minus suction temp, but that would be at the true suction port right? both my temp probe and gauges should be on true suction.
Old 03-19-2014, 04:25 PM   #58
An old Tradesmen
Yeah, low side connected to true suction, but the temp probe connected just after teh evap. Don't want to have it connected after the RV, as it will have gained some temp going through the RV.
Old 03-19-2014, 04:34 PM   #59
with the subcool being -30 that tell me there is no liquid in the liquid line, right? The condenser is not condensing, right? The numbers look ok(maybo a little over charged now) but all of my temps are way off. I even swhitched temp probeds
Old 03-19-2014, 05:14 PM   #60
An old Tradesmen
A -30 SC, generally indicates a problem with either the gauge, or the temp probe. Or, there is a heater on, heating the refrigerant.
But, with a 2 ton rated coil and blower on a 3 ton heat pump, its possible your not removing enough heat to condense.
3.5ton evap with 4 ton compressor wetbar HVAC 1 06-15-2013 04:41 PM
15 degree split, scroll compressor is hot!! bobinphx HVAC 1 06-05-2013 04:30 AM
Help assembling compressor jfhspike Tools 5 03-27-2011 10:07 AM
Air compressor and framing nailer for DIY ADKstorm Tools 20 11-11-2010 07:38 AM
New Compressor - Wrong Charge? shayneb HVAC 4 08-23-2008 08:13 AM