24v Not Present At Terminal Block Or Tstat Wire Leading To Condenser Outside? - HVAC - Page 2 - DIY Chatroom Home Improvement Forum
Old 01-16-2013, 11:41 PM   #16
Originally Posted by sammy37 View Post
I thought about telling him to check Y to C at the stat also but the problem is most newer stats lose connection when you remove them from the base.
He has said that the air handler does run, so I'm thinking either bad stat, or bad wire between stat and air handler.
If he has an extra spare wire in his cable, he could easily hook that in place of the yellow at each end and then he would at least be able to narrow it down to a final problem.
Yeah hopefully he has the kind that you can remove the cover and test the wires in place. Otherwise the stats are somewhat difficult to check. But if thats the case simply jumping R to Y and seeing if the cond unit came on would tell him if it's the stat or not.
JScotty is offline   Reply With Quote
Old 01-16-2013, 11:57 PM   #17
Rewards Points: 484
Correct, didnt think about that.
sammy37 is offline   Reply With Quote
More than one wire on bus terminal? Ultrarunner2017 Electrical 5 02-01-2009 11:55 AM
Neutral Wire? 4x15mph Electrical 8 11-24-2008 01:00 PM
Which wire from the main breaker to the A/C condenser? slwalsh HVAC 2 10-15-2008 01:33 PM
hooking up dryer....bronx ny code SURFBUG Appliances 6 10-14-2008 09:41 PM
Dryer Grounding??? Traci_howdyadothat Electrical 7 05-27-2008 01:14 PM