2008 York Modulation Furnace PM9C Issues - HVAC - Page 3 - DIY Chatroom Home Improvement Forum
Old 12-19-2013, 07:24 PM   #31
AKA HVACTECHFW
Rewards Points: 1,208
There is no reason to go after york.... the product works as designed. The problem (as much as you might not like it) is probably due to installation.......just saying....
IT IS WHAT IT IS
hvactech126 is offline   Reply With Quote
Old 12-19-2013, 08:55 PM   #32
Another DIY Zombie
Rewards Points: 264
Just tried this test....
So again, at 9pm, the furnace ran nice and slow then ramped up to full and blew cold air. I did not even go look and verify the 3-red flashes. I simply went to the tstat and turned the setpoint to below ambient and it shutdown. Then I set it back up to the previous setpoint and it worked perfect. now the question.
Is there a programmable tstat out there that allows the setting of both high and low temps? So for example, I can have it set for 67 during the day, but if it drops below 64, it will shutdown. Just a guess. I am also looking into a tstat that I can access via the internet since I tend to travel a lot for work. It would be nice to be able to see what is going on at home when I am on the road....
javan is offline   Reply With Quote
Old 12-19-2013, 08:56 PM   #33
Another DIY Zombie
Rewards Points: 264
I tend to agree on the installation issues, but......
Why does it continue to run on full fan with no flame........It just boggles the mind!
Old 12-19-2013, 09:01 PM   #34
AKA HVACTECHFW
Give it up! It is what it is... nothing is going to change how it is designed to operate.
IT IS WHAT IT IS
Old 12-19-2013, 10:02 PM   #35
Hvac Pro
yuri's Avatar
Rewards Points: 92
I suspect for some reason York thinks that any error code like that is like an open limit switch and may be wired in the same way. when a limit switch opens the board is programmed to run the fan to "cool down" a possibly overheated heat exchanger. they may be trying to protect the heat exchanger and overcautious. I am not going to debate whether that is a good idea or not. I also suspect you may have a faulty board. Don't know if that full blast fan scenario is unique to yours or they all do that as I don't do a lot of York.
Old 12-20-2013, 04:17 AM   #36
An old Tradesmen
Rewards Points: 7,770
No, as that would defeat the 4 hour anti freeze timer many furnaces have.
Look into Ecobee.
Old 12-20-2013, 07:40 AM   #37
Another DIY Zombie
Rewards Points: 264
last night at 1:30 am. Furnace comes on for 1 minute with inducer fan running, dist fan ramps to 100%, then shuts off, immediate restart attempt. It did this 4 times in a row before I stepped in and reset it. Then it ran fine until I left this am.
Old 12-20-2013, 07:56 AM   #38
AKA HVACTECHFW
Replace the control board
IT IS WHAT IT IS
Old 12-20-2013, 02:13 PM   #39
Another DIY Zombie
Rewards Points: 264
Talked it over with the Tech and he agrees that it is most likely the CB. He does want me to change the jumper settings for the ATR though and see how it behaves. He said that he has never heard of the scenario that I have been encountering (Furnace comes on for 1 minute with inducer fan running, dist fan ramps to 100%, then shuts off, immediate restart attempt)
Old 12-20-2013, 04:25 PM   #40
AKA HVACTECHFW
I personally saw that exact problem on your model furnace on Monday. I replaced the control board and there have been no problems since.
IT IS WHAT IT IS
Old 12-20-2013, 04:33 PM   #41
Hvac Pro
yuri's Avatar
Rewards Points: 92
Does the board have a 10 yr warranty? If so it may have to be replaced by a York dealer to get the warranty as he has to fill out the fault symptoms on the warranty card and they may or may not approve it if it is not consistent or documented/described properly.
Old 12-20-2013, 04:37 PM   #42
AKA HVACTECHFW
I doubt warranty is valid to due to homeowner installation.........
IT IS WHAT IT IS
Old 12-20-2013, 04:46 PM   #43
Hvac Pro
yuri's Avatar
Rewards Points: 92
If his father in law is a contractor and the tech is willing to try they may get away with it. probably the tech will put "subject to approval from York" on his invoice and charge him for it and re-imburse him later if it goes thru. bit different than Joe DIYer trying it on his own.
Old 12-20-2013, 04:49 PM   #44
AKA HVACTECHFW
I will agree to disagree with this statement. While a contractor he may be.... that does not show his competence in HVAC.
IT IS WHAT IT IS
Old 12-20-2013, 05:10 PM   #45
Hvac Pro
yuri's Avatar
Rewards Points: 92
I know, just trying to help him, it is a DIY site after all. Good Karma also as someone will help me later. The manufacturers don't always give you a credit just because you handed a part in and rightfully so, it should be tested. I hate parts changers and especially parts changing techs when I have to clean up their crap.
The Following User Says Thank You to yuri For This Useful Post:
hvactech126 (12-20-2013)
Seeking help with Furnace Issues atdwest HVAC 7 11-27-2013 05:03 PM
York furnace problem brucem609 HVAC 7 11-03-2013 06:35 PM
Brand New Concord Furnace Doesn't Work In Cold Weather LeighC HVAC 21 01-07-2013 08:48 PM
York vs Rheem furnace venting raylo32 HVAC 6 08-30-2011 04:28 PM
York Furnace Leaking.. Please help sidoe HVAC 4 10-08-2007 04:55 PM