I have a Hydronic system that currently is running one manifold with two loops. I am adding one more manifold with 4 loops. I want to control each manifold with a zone valve. One manifold is for a small room where the temperature will be warmer than the other. My intentions are to open the zone valve 1 and fire the boiler with one thermostat and the open zone valve 2 and fire the boiler with the other thermostat.
-------ZV1----------Thermostat1
B
-------ZV2----------Thermostat2
My question is will this work or will I have a problem if both thermostats send voltage at the same time? This is a 24V system. Do I need a relay?
screwy is offline   Reply With Quote
Old 12-30-2011, 06:19 AM   #2
AKA HVACTECHFW
Rewards Points: 1,208
the zone valves will be tied together or piggy backed sending the call for heat signal to the boiler. I would add an additional transformer to run the zone valves though, probably 75VA.
IT IS WHAT IT IS
hvactech126 is offline   Reply With Quote
The Following User Says Thank You to hvactech126 For This Useful Post:
screwy (12-30-2011)
Old 12-30-2011, 08:44 AM   #3
The zone valves say that they use only 2Va, each the transformer is a 40Va, would you still recommend an additional transformer for a total of 4Va?
Old 12-30-2011, 09:16 AM   #4
biggles's Avatar
just wire each zone valve as if it is the only one when the stat calls the zone it swings end switch makes the cirulator and burner if the water is below setpoint within the boiler.the VA concern is the run out to the stats if there digital they might pull on the zone valves or chatter the circ/boiler relays wire it up and see if anything drags with the entire show running.once #1 ZONE valve/end switch calls the rest are going to follow from each stat so the circ/bolier will already be running...then on stats being satisfied the last stat will shut the show down once the valve closes and the switch opens..the TR on the boiler will handle the zones valves,but the stats are the drawalso in the VA totals
Old 12-30-2011, 05:28 PM   #5
AKA HVACTECHFW
I like to add the additional transformer to cover my butt. Oversizing the Xfmr will not cause a problem and it leaves you plenty of room for add-on's later. Even if you add an additional 40Va xfmr it wont hurt anything. This also keeps the the zones valves isolated from the ignition circuit.
IT IS WHAT IT IS
Boiler's 24VAC overloaded? BenOwner HVAC 7 12-11-2011 06:30 AM
Setting the reset "Curve" for a modulating boiler (modcon) mknmike HVAC 5 02-10-2011 12:37 PM
Need help fast please re hydronic boiler water supply and backflow DanDaMan HVAC 6 12-11-2010 03:26 PM
I Need a New Boiler. What do i need to know New Boiler Co Plumbing 0 10-23-2010 07:03 PM
Burnham boiler banging/thumping noises quadradeuce HVAC 6 10-02-2010 10:55 PM