So if R12 run around a 20-16 psi suction @ 15-20 degrees.
What should a 134A frige. run at?
I have a little prep. station/frig. that the compressor is running all the time and it will only get down to 50 degrees.
beenthere 07-31-2010 06:57 AM
14 to 18.
jomama 07-31-2010 01:29 PM
if your suction pressure is that low and box temp at 50 what is discharge psi
beenthere 07-31-2010 03:56 PM
I don't think he said his vapor pressure is that low.
mikethe ductman 07-31-2010 06:45 PM
I just took a look at the unit.
Box temp was around 50, suction pressure around 12-13 and cond. coil was dirty.
I cleaned the coil but little to no change on suction pressure.
Eased a littlr R134 in, got the suction pressure up to 18.
Looks like its not the first time being toped off, king valve looked a little chewed up.
I will follow up on it Monday to see if its working better.
beenthere 07-31-2010 08:19 PM
Did you check the SH and SC?
At temp, the vapor line will be around 14 to 18.
On a warm box, it will be around 28 to 30.
mikethe ductman 08-02-2010 06:46 PM
I went back by today.
The temp droped to 38 degrees.
The owner had replaced the t-stat some time ago.
He said it was set at 22 degrees
I don't know if the system will pull down that far, he keeps the unit between an oven and a pizza oven.
I will recheck the pressures next week.
beenthere 08-02-2010 06:48 PM
LOL... pizza shop. Get the cheese and flower out of the condenser.
jomama 08-03-2010 01:05 AM
he will need a jackhammer that stuff is like cement