Building Soffit - Carpentry - DIY Chatroom Home Improvement Forum
Old 11-18-2009, 12:38 PM   #1
building soffit
building a room in my basement ..need to build soffit to cover 2 heat ducts a waste water pipe and steel support beam ..they are close enough together so I will be building a 6' x 14' soffit to cover them ....if I do it out of 2 x 2 's will the 6' span bow ?.... I cant support it in the center because of heat duct ....guess if I had to I could make two soffits but I think it would look better with one ..thanks
44070dart is offline   Reply With Quote
Old 11-18-2009, 12:44 PM   #2
Remodeling Contractor
it will bow. Support at the center with threaded rod into a screw in stud anchor. This way you can use a driver to insert the rod in between the two ducts from below. Set the nuts into the studs to keep it all flush.
Old 11-18-2009, 02:05 PM   #3
Registered User
Rewards Points: 4,890
2x4 with a 10# live load (ceiling joist) will span 7'2" at 24"on center. The 5/8" drywall needs 24"o.c. also, if you wet texture it.
Be safe, Gary
Old 11-18-2009, 04:39 PM   #4
OP said using 2X2 and will it sag?? did I miss something?
Old 11-18-2009, 07:06 PM   #5
threaded rod ... why didn't I think of that ...thank you
Old 11-18-2009, 07:32 PM   #6
Registered User
"if I do it out of 2 x 2 's will the 6' span bow ?" ---- Yes, as Bob already said it will bow.
"I cant support it in the center because of heat duct " ---- So your span is 6'. Minimum residential code for ceilings is 2x4 for a 6' span. I don't have load ratings for 2x2 anywhere, but if you took 1/2 the span for the 2x4 I said earlier, it would only be 3'7".
Drywall, 1/2", weighs 2.2# per square foot, so your 6' x 2.2# x 24"o.c.= 26.40# 5/8" drywall is 33#.
If 16"o.c., is 17.69# 5/8", 16"o.c. is 22.11# http://www.bc.com/dms/wood/ewp/3_Gui...0Materials.pdf
Be sure to read the footnotes below and go to the article as it may answer other questions you might have:
Table 1
Maximum Framing Spacing
For Single-Layer Gypsum Panel Product
Gypsum Panel Gypsum Panel Maximum
Product Thickness Product Orientation Framing Spacing
in. (mm) to Framing in. (mm) o.c.
Ceilings:
3/8 (9.5) A Perpendicular B 16 (406)
1/2 (12.7) Parallel B 16 (406)
1/2 (12.7) Perpendicular B 24 (610)
5/8 (15.9) Parallel 16 (406)
5/8 (15.9) Perpendicular 24 (610)
Walls:
3/8 (9.5) Perpendicular 16 (406)
or Parallel
1/2 (12.7) Perpendicular 24 (610)
or Parallel
or Parallel
A Shall not support thermal insulation.
B On ceilings to receive hand or spray-applied water-based texture
material either i) 1/2 in. (12.7 mm) gypsum ceiling board (ASTM
C 1396/C 1396M shall be applied perpendicular to framing; or ii)
other gypsum panel products shall be applied perpendicular to
framing and board thickness shall be increased from 3/8 in. (9.5
mm) to 1/2 in. (12.7 mm) for 16 in. (406 mm) o.c. framing and
from 1/2 in. (12.7 mm) to 5/8 in. (15.9 mm) for 24 in. (610 mm) o.c.
framing. See Appendix A.2. From: http://www.gypsum.org/pdf/GA-216-07.pdf
Ah, Bob hit the nail on the head between my answer, Good job, Bob!.
Be safe, Gary
Old 12-17-2009, 10:40 PM   #7
I am glad that I found this thread because I have a very similar situation as OP.
I am finishing my basement, already done most of the framing. Only have some soffits left. The heat and cold return trunks in my basement run next to each other with about 2 inch gap between them, and the span is about 4 - 5 feet. My plan is to use 2x2 for the joist ledger, and 2x4 lookout in 16 in o.c. Will this be strong enough? Does the joist ledger need to be 2x4 too?
As far as using threaded rod to support the center, I don't have a clear picture of how it would be done. Could you please explain a little bit more?
Thanks in advance
(Attached is a picture of the trunks)
xuc318 is offline   Reply With Quote
Old 12-18-2009, 08:22 AM   #8
I believe this is what they are trying to say to do.
as you can see the wood goes around the ducts and a threaded rod goes from the floor joists between the ducts and you bolt the cross 2 x 4 through it.
baum is offline   Reply With Quote
Old 12-18-2009, 08:30 AM   #9
The threaded rod can be screwed into a threaded lag bolt that is made for this purpose. The nuts at the bottom get recessed into the studs so the drywall is flush.
Old 12-18-2009, 03:11 PM   #10
Registered User
Please read the fire-blocking article here: How to fireblock framing
You need it at the soffit line in the wall to stop a fire (maybe from an outlet) from leaving the wall cavity into the soffit/mechanical chase easily and quickly spreading to distant parts of the house unseen.
Be safe, Gary
Old 12-18-2009, 06:37 PM   #11
Thanks for the replies. The picture doesn't show how the top end of the threaded rod is attached to the floor joist. Is it screwed to the lag bolt which hangs between floor joists? And if I use 2x4s, will it be strong enough without the threaded rods?
GBR, I read the fire-blocking thread several times. Very informative. I already fire blocked the gaps between top plates and the wall. Do I still need to fireblock at the bottom of the soffit?
Old 12-18-2009, 07:53 PM   #12
Registered User
Yes, the new ceiling/wall level is at the soffit bottom. Picture a fire behind the drywall in a stud cavity. It can go up the wall, into the tin-work chase from the wall side. Then anywhere the tin-work goes AND into each ceiling/floor joist bay anywhere across the length of the chase, popping up next to a floor register above, or up to the next floor - if not fire-stopped there.
Be safe, Gary
Old 12-18-2009, 08:07 PM   #13
wish i had the ability to post pics like some of the smart folks here so i will try to do with words. they make a lag with a threaded end for nuts. In this case you could add a coupling with a piece of allthread rod to the length you need and run it into the joists between the duct. To get the torque you need to set the lag part thread two nuts together and they should stay in place while tightening
Old 12-18-2009, 09:15 PM   #14
Tpolk, you have pictures showing how the rod is attached to the joist? I am new to home improvement work, still doesn't have a clear picture of how it would be done.
Posting picture is easy. When you reply a post or create a new one, in the section of 'Additon Options', click on 'Manage Attachments', then browse the pictures in your computer, and upload. Or email the pictures to me if you could.
Thanks a lot.
Old 12-18-2009, 10:24 PM   #15
firehawkmph's Avatar
Rewards Points: 1,792
Dart,
I have used 1 x 6 T&G pine to span the hvac trunklines like you show. I build a 2 x 4 wall on each side a 1/2" below the lowest hanging structure. The pine easily spans it and looks nice to boot.
Mike Hawkins
firehawkmph is offline   Reply With Quote
Help with installing aluminum soffit and fascia Boontucky Roofing/Siding 3 09-01-2009 08:47 PM
Building a soffit around a drainage pipe along the wall ssudha17 Building & Construction 12 10-04-2008 04:18 PM
building a soffit can I use 2 X 2s yummy mummy Building & Construction 13 11-14-2006 08:57 AM