can i use 2x4 as roof rafters on an 11x9 shed with a ridge beam? someone told be 2x6 but i am thinking if i use a 2x6 beam in the middle and then 2x4 rafters, that should be enough.
thoughts?
rditz 01-11-2011 12:19 PM
2x4 for that span is fine... make sure you have a decent pitch, will will help with snow shedding..
rod
amakarevic 01-11-2011 01:16 PM
i was gonna go with only about 17 deg pitch because i don't want the roof to rise higher. i live in DC so not a whole lot of snow. do you think 2x4 will be sufficient to sustain 2 ft of snow at that low of a pitch? if not i can totally go with a 2x8 ridge beam and 2x6 rafters. what do you think?
rditz 01-11-2011 01:22 PM
absolutely no problem..
I live in Ontario and we get a decent amount of snow. my 20x20 garage is a raftered roof and it is done with 2x4's
go for it.
rod
Gary in WA 01-11-2011 03:54 PM
Just make sure to use #2 grade lumber as #3 in SPF will only span 5'5". With that low a pitch (3.25) you are very close to 3/12 and lower pitch requires a ridge beam; http://publicecodes.citation.com/ico...002_par017.htm
http://www.awc.org/calculators/span/...orizontal+Span
If rafters span the 11’ and the ridge beam would be a 9’- 2x10 or 2-2x8’s for the 2475# load maximum using doug-fir (N).That is using your local 25# ground snow load.