Just finished laying the forms for our stepped footer today and am going to get the footer rebar put in tomorrow morning.
1) Is vertical rebar generally required for footer inspection (before pour)?
2) Does the vertical rebar need to run completely to top block or just to grade?
3) How many feet should it be spaced apart?
stevekem is offline   Reply With Quote
Old 06-08-2013, 10:02 PM   #2
Rewards Points: 4,792
the rebar is horizontal in a foundation,,, 4' o/c # 5 bar in block for bsmt walls,,, i'd put in tie bars in a stepp'd footer.
stadry is online now   Reply With Quote
Old 06-08-2013, 10:08 PM   #3
concretemasonry's Avatar
Rewards Points: 2,640
In a "stepped footing", the rebar is intended to provide structural continuity up/down and across a section. Usually, bends and lapping distance between vetical steel are required. This is because it is necessary to distribute the loads as the elevation and loads change depending on the situation.
Inspection requirements depend on the local requirements, so the local inspection office should be contacted, since different jurisdictions are allowed to enforce them.
Are you sure the rebars are not just dowels to connect to higher parts of a wall to be built later? (either block or concrete).
Dick
concretemasonry is online now   Reply With Quote
Old 06-08-2013, 10:22 PM   #4
Rewards Points: 184
Yes, I was referring the vertical rebar sticking out of footer for the block wall to go over. Is this generally required to be in place for footer inspections?
Regarding the stepped footer, I have 1 step that goes down 24" exactly to lower footer. I was going to have 2 runs of horiziontal rebar throughout footer and tie into the 2 runs of vertical rebar in "step" using rebar tie wire. Would this be ok or do I have to bend the rebar at 90 degrees to follow "step" down into lower footer?
Dick
Old 06-09-2013, 07:36 AM   #5
Old School
Willie T's Avatar
Yes, bend them. And it isn't exactly a full 90° / 90° bend... just as the drop-off should not be sheer 90° turns. The top part should be dug back to create a 45° slope down into the lower portion, and the rebar bent to match the angle.
9 times out of 10, the AHJ is going to want to see the vertical dowels in place before passing the footer. And in some areas, the code calls for specific placement. (exact measurements)
Willie T
Old 06-09-2013, 07:55 AM   #6
Concrete & Masonry
Rewards Points: 636
Here it isn't, but you may want to have your bent rods ready to go so the inspector can see them.
Just run dowels for now and set the rest of the length after the footings hard, or after you lay the block.
Depends on a number of factors. The same code that's requiring you to install vertical rebar should give you the specifics on size, spacing, etc...
jomama45 is online now   Reply With Quote
Old 06-09-2013, 07:57 AM   #7
Concrete & Masonry
Rewards Points: 636
What Willie said.................
Size Rebar Needed to Reinforce Bowed Block Wall frtools Concrete, Stone & Masonry 7 06-18-2012 11:28 AM
Vertical Rebar Layout in Block Wall Footing 99altrade Building & Construction 6 08-12-2011 09:32 PM
# of rebar in cinder block wall johnlvs2run Building & Construction 3 08-08-2010 10:48 AM
Rebar for Monolithic Slabs portert0224 Building & Construction 1 07-03-2008 11:37 PM
Vertical rebar support. jrepp Building & Construction 6 11-22-2007 05:28 AM