Insulating under porch
Yes, we sprayed over the wood and the walls. Since this is a storage/utility area, we did not get this part officially inspected yet, so I'm not sure whether the walls need to be covered.
The datasheet reads as follows:
FL 2000 is a Class I formulation, as Tested per ASTM E84, and at a
thickness of 4.0 inches possesses the flammability characteristics shown
below:
ASTM Method E84 Class I
Flame Spread ≤25
Smoke Development ≤450
4.3 Thermal Barrier:
The Foam-Lok FL2000 spray foam insulation must be
separated from the interior of the building by an approved
thermal barrier of minimum 1/2-inch-thick (12.7 mm)
gypsum wallboard or an equivalent 15-minute thermal
barrier complying with, and installed in accordance with,
IBC Section 2603.4 or IRC Sect ion R316.4, as applicable,
except when installation is in attics and crawl spaces as
described in Section 4.4. Thicknesses of up to 12 inches
(305 mm) for ceiling cavities and 12 inches (305 mm) for
wall cavities are recognized, based on room corner fire
testing in accordance with NFPA 286.