Originally Posted by Ravenworks View Post
Fire board is fire rated drywall such as 5/8" either way you need a fire break on the wall.
Really? I don't think I've ever seen drywall inside an unfinished attic.
Jeremy Hillary Boob, PhD is offline   Reply With Quote
Old 03-02-2012, 10:54 AM   #17
Exterior Construction
Windows on Wash's Avatar
Rewards Points: 3,286
Doesn't necessarily require drywall but it will have to be either approved or require a specific ignition barrier.
Fiberglass may be suitable.
http://sprayfoam.com/leps/letitem.cfm?letid=37
Old 03-02-2012, 12:33 PM   #18
As I read it, this deals with commercial buildings, not residential. Did I miss something?
Old 03-02-2012, 12:59 PM   #19
Yes.
Ignition Barriers: When foam plastics are used in attics and crawlspaces, they still must be separated from the interior space with a thermal barrier. However, in attics and crawlspaces where entry is only for service of utilities (not used for storage or living space), the foam plastic may be separated from the space in the attic or the space in the crawlspace with an ignition barrier instead of a thermal barrier.
Code designated ignition barriers include:
  • 1-1/2 inches of mineral fiber insulation (rockwool or unfaced fiberglass)
  • 1/4 inch of wood structural panels
  • 3/8 inch particle board
  • 1/4 inch hardboard
  • 3/8 inch gypsum board
  • Corrosion resistant steel having a base metal thickness of 0.016 inch.
Old 03-02-2012, 02:58 PM   #20
Yes.
Well, I'm still not getting it. I thought the IBC was for commercial buildings, while the IRC applies to residential. The link (and quote) you give seem to be from an IBC document.
Old 03-02-2012, 04:39 PM   #21
IRC Section 316.5.3 states the following:
Exceptions to the Thermal Barrier Rule: There are exceptions to the thermal barrier requirements in the IRC code listed in Section 316.5. The following items are a few examples listed in the IRC code.
  • Foam plastic covered a one inch thickness of concrete or masonry
  • Foam plastics used in roofing applications (although roof coverings must be tested using other methods.)
  • Bare sprayfoam 0.5 to 2.0 lbs per cubic ft density (open or closed cell) can be installed without a thermal barrier to sill plates and headers so long as the foam is a maximum thickness of 3.35 inches, has a flame spread rating of 25 or less and a smoke developed rating of 450 or less in accordance with ASTM E-84.
  • Attics and crawl spaces do not require a thermal barrier and can use an ignition barrier instead.
Code designated (prescribed) ignition barriers include:
Old 03-02-2012, 06:11 PM   #23
OK, got it.
It looks like that might be more trouble than it's worth. So, maybe I'm back to square one---cover the fiberglass batts with Tyvek and be done with it...
Old 03-02-2012, 06:44 PM   #24
Not that big and issue.
Cover it with some unfaced fiberglass and you are all done.
Old 03-03-2012, 12:08 PM   #25
Registered User
Rewards Points: 5,498
Or, just install some Thermax , tape the seams with foil tape. Ask your local AHJ about this to be sure.
http://www.icc-es.org/reports/pdf_files/NES/NER681.pdf
Gary
Old 03-03-2012, 01:07 PM   #26
Ravenworks's Avatar
I had to put 5/8's drywall on mine to pass inspection,regardless if I used foam or not.
That is just how the inspector wanted it.
It wasn't a big deal at the time because I had the walls opened up which gave me plenty of access. At the time it seemed like it was over kill.
Ravenworks is offline   Reply With Quote
Old 03-03-2012, 11:16 PM   #27
Gary
That looks like the best idea so far. Thanks.
Old 03-04-2012, 08:58 AM   #28
Gary
Btw, does anybody know where to get this stuff? A local Home Depot used to carry it, but not now.
Old 03-04-2012, 12:36 PM   #29
Most big box stores have it.
All you are looking for is a foil faced poly-iso.
Fixing multiple attic electrical issues before blowing in insulation darlingm Electrical 11 11-19-2011 09:19 AM
Attic project - Would like opinions whataboutj Insulation 6 06-29-2011 03:07 PM
Air sealing, ventilation, and attic insulation project-need advice Badfish740 General DIY Discussions 4 06-01-2011 06:48 AM
Adding insulation and storage to Cape Cod Side Attic turin39789 General DIY Discussions 5 11-08-2010 10:50 AM
Extending finished attic insulation stops? Mitch H HVAC 2 12-09-2009 11:00 AM